    Our water pressure regulator is broken and I forgot where we bought the first one. Anyone know where to get one in Duma?

    (As we have sediment filter and water softener on all incoming water we need to reduce the pressure to the maximum 120psi those tanks can handle without blowing up, so a regulator that reduce frequent over pressure is needed).

     
  2. Best Answer:
    Post #3 by ShawnM, Mar 31, 2015 (5 points)
  3. Jack Peterson

    Jack Peterson DI Forum Luminary Highly Rated Poster SC Connoisseur Veteran Air Force

    Messages:
    9,080
    Trophy Points:
    451
    Occupation:
    Happily Retired
    Location:
    Northern Junob, Dumaguete City
    Ratings:
    +5,209 / 1,086
    Matao would be my Suggestion but I do remember seeing them at City Hardware. ( They have an extensive Plumbing section there) if that end of town by Robinsons, AS building suppliers next Door also have Plumbing Stuff
     
    • Informative Informative x 3
  4. ShawnM

    ShawnM DI Forum Patron ★ No Ads ★ Highly Rated Poster Showcase Reviewer Blood Donor Veteran Air Force

    Messages:
    1,504
    Trophy Points:
    371
    Occupation:
    Senior Construction Manager
    Location:
    Okinawa/Tanjay
    Ratings:
    +1,752 / 218
    Blood Type:
    A-
    Best Answer
    Polaris has a very good selection of plumbing parts and would be my best recommendation for a pressure reducing valve. I am curious on your set up where you are getting 120 PSI. 95 PSI is normally the max for a commercial building, 120 would ruin most fixtures.

    Shawn
     
    • Agree Agree x 3
  5. OP
    OP
    denpet

    denpet DI Senior Member Highly Rated Poster Blood Donor Veteran Air Force

    Messages:
    581
    Trophy Points:
    186
    Ratings:
    +351 / 96
    Blood Type:
    O+
    Yes, I would probably put it below 100 too. The tanks are rated 120psi that's why I wrote that. I guess there are some margin on them, so they could handle some excess pressure. But now, the pressure sometimes exceeds 200 !!!
    The fixtures is not a problem in our case though, as we just fill up an elevated tank and let gravity pressurise the resort. But, the filters are before the tank.
     
    • Informative Informative x 2
    • Like Like x 1
  6. ShawnM

    ShawnM DI Forum Patron ★ No Ads ★ Highly Rated Poster Showcase Reviewer Blood Donor Veteran Air Force

    Messages:
    1,504
    Trophy Points:
    371
    Occupation:
    Senior Construction Manager
    Location:
    Okinawa/Tanjay
    Ratings:
    +1,752 / 218
    Blood Type:
    A-
    OK, I think I understand your set-up. I would definitely reduce that pressure ASAP, 200 PSI is dangerous, a ruptured tank would suck. How are the filters holding up being before the tank? I was worried with my little set-up at the house and put the filter after the tank (gravity as well so a much lower pressure).

    Shawn
     
    • Informative Informative x 1
  7. OP
    OP
    denpet

    denpet DI Senior Member Highly Rated Poster Blood Donor Veteran Air Force

    Messages:
    581
    Trophy Points:
    186
    Ratings:
    +351 / 96
    Blood Type:
    O+
    One is on order from Polaris now. Found now place where they had it in stock. The filter tanks keep up so far.
     